Evening all,
Need some help with a generator sizing.
Incoming service is 600A 3P 480/277 4wire.
That feeds a sub panel with a main breaker at 150 3P480/277v 4 wire.
Off that panel is a 30KVA 3phase step down transformer 208/120Y secondary which feeds a 100A 3phase 208/120 panel. That transformer if I did my math correctly outputs 83.3 Amps.
Each leg of that panel is 6A, 17A, 31A.
They want a generator to handle (8) 120V circuits from various panels which feed CCTV, door swipe etc systems. I do not know the actual draw of each of these circuits but likely not much.
Question
What size generator and ATS can be supported from that 120/208v 3phase panel. They wanted a 20KW generator which I think would require 100A and that would be to big.
2nd question
Option B is coming off that 150A 277/480 panel but I think then I need another 30KVA 208/120 transformer or larger to support the 20KW generator and (8) 120V loads which will be placed in a separate panel connected to the ATS.
I'm stumped on how best to achieve the end goal of having these (8) 120A loads protected with the generator.
The 20KW request was room for growth but also based by the customer on a 120/240v single phase system.
He wasn't aware is a 3 phase service.
Any assistance would be greatly appreciated
Need some help with a generator sizing.
Incoming service is 600A 3P 480/277 4wire.
That feeds a sub panel with a main breaker at 150 3P480/277v 4 wire.
Off that panel is a 30KVA 3phase step down transformer 208/120Y secondary which feeds a 100A 3phase 208/120 panel. That transformer if I did my math correctly outputs 83.3 Amps.
Each leg of that panel is 6A, 17A, 31A.
They want a generator to handle (8) 120V circuits from various panels which feed CCTV, door swipe etc systems. I do not know the actual draw of each of these circuits but likely not much.
Question
What size generator and ATS can be supported from that 120/208v 3phase panel. They wanted a 20KW generator which I think would require 100A and that would be to big.
2nd question
Option B is coming off that 150A 277/480 panel but I think then I need another 30KVA 208/120 transformer or larger to support the 20KW generator and (8) 120V loads which will be placed in a separate panel connected to the ATS.
I'm stumped on how best to achieve the end goal of having these (8) 120A loads protected with the generator.
The 20KW request was room for growth but also based by the customer on a 120/240v single phase system.
He wasn't aware is a 3 phase service.
Any assistance would be greatly appreciated