meleconn
Member
- Location
- stuart, fl
a customer (gas station / conv store) has a 600 a 3 ph 208V system w/ a demand load of 317 A, 1- 600 A 3 ph main disconnect w/5 - 200 a disconnects for interior panels, 1 - 200 A 3 ph disconnect for 1 -3 ph panel tapped off from main disconnect... he bought a 100 kw gen w/ a 400 ats. wants to run everything (recvd info from another electrical co. on purchasing this equip.) I think he needs either a 600A ats to connect to main disconnect (to connect to all) , but if that is the case then he should have a gen capable of 600 A output. if he goes w/ a 400 A ats then the 400 A ats should be w/ load center. cannot find 400 ats w/ load center capable of having 2- 200A breakers to connect to 2 disconnects.. he really wants all of the disconnects to be connected but I do not see where the 400A is capable / code wise. i believe that connecting the 400 ats to the disconnect will be wrong as the overcurrent fuses will be too big, & connecting all the 200 A disconnects to it will be cause fro overload. any suggestions /help is appreciated. thanks mikep