Are there any VFDs that are suitably listed for use with fire pumps?
It is not something that I recall hearing about.
NFPA 20 recognizes the existence of VFD's when discussing soft start units in 10.4.5.5.
Here is a link to one controller providing this feature.
Would you please provide some more details for your calculations in equations assuming that we have 100hp fire pump?The running load calc would be the same 125% FLA.
Soft starts typically limit to 300% in-rush. This is helpful for starting voltage drop (max 15%), which does reduce the genset size. Typical locked rotor is 5x. This means that there is a possible reduction in genset by about 1.6x.
NFPA 20 also discusses a requirement for emergency start function (across the line). We don’t have to meet the 15% during this condition, but we still need the controls to work, i.e. - we at least stay above 30% voltage drop to avoid electronics under voltage drop out. This needs to be considered as well.
But the VFD should not have any overload protection for the fire pump.
One problem with VFD is it introduces distortion so much so that any reduction in size of the generator due to lower starting kW and starting KVA is offset by it.
So the answer to OP is no.
Thank you, but really i don't understand how we get 1.6 or any possible reduction in generator sizing due to soft starting.Your 100HP across the line:
Same issue as in VFD- Distortion, but may be overcome if bypassed after starting.The worked example came up with 450kW in the across the line example and 250kW in the soft start. 450/250 = 1.8. Or you can look at it as ~40% reduction in generator size.
If you had read the information at the link, you would have seen that's exactly what happens.