I have an existing building with peak recorded demand at the utility meter 700kW in June 2022. 400kW of load will be added to the facility including heat pumps, boilers, new medical equipment, etc. (this is a hospital in WI).
- Per NEC 220.87 (2), to size a generator that backs up the entire facility, should I calculate the existing demand x1.25 then add the new 700kW, or multiply the sum (400+700)x1.25? It would differ by a 100kW.
- The facility has 2 existing parallel generators, rated at 500kW each, which back up all electrical loads except for a normal distribution panel and a 1000A chiller panel that powers 3 chillers, each rated at 350kW and has a 500A breaker in the chiller panel. If I were to size the generator such that one chiller is supported, I am assuming that half of the 700kW is actually cooling load (reported in June), so the three chillers are functioning at 1/3 capacity, but to backup one of them I would assume full capacity of one chiller?