What is the requirement for sizing of the generator and ATS.... can the unit be undersized and still be automatic with load shedding.
What is the requirement for sizing of the generator and ATS.... can the unit be undersized and still be automatic with load shedding.
I should mention that it is res. and the HO wants to have automatic transfer and manage load
Shedding .... 400 amp service ... 200 amp service rated ATS.... 2- 200 amp panels with a 20kw gen set that is way undersized ( HO already purchased system and want install ).. I guess my question is will tha AHJ allow the HO to manage the shedding manually ?
I should mention that it is res. and the HO wants to have automatic transfer and manage load
Shedding .... 400 amp service ... 200 amp service rated ATS.... 2- 200 amp panels with a 20kw gen set that is way undersized ( HO already purchased system and want install ).. I guess my question is will tha AHJ allow the HO to manage the shedding manually ?
I've done this type of system and it's usually rather easy. As someone above mentioned, install the 200A ATS before one of the panels, then move circuits between the panels to suit your needs. Afterwards, do a load calc.
At this point you may be ok with the 20kw generator, depending on the results of the load calc. If not, then use a method of load shedding.