I am sizing a generator for a decent sized house. It has a 200 amp service with a 125 am sub panel next to the main service. All the generator loads are in the 125 amp panel.
I calculated the load on the 125 amp panel at 98 amps using the optional calculation AC larger than heating. The loads are as follows:
General lighting 2774 sq ft @ 3va=8322va First 10000@ 100%= 10000
cook top 5800 Remainder (total-AC load-10kw) = 18888 @ 40%= 7555.20
dryer 5000 AC load @ 100%= 5904
well pump 1656 Total= 23459.20/240 volt=98 amps
disposal 850
dishwasher 1320
Boiler (runs for DHW) 1440
laundry 1500
2 small appliance 3000
AC 5904
Total 34792
I used the square footage @3va for the entire house which gives me a little fudge factor as not all the general use circuits are on the sub panel.
They are using a portable generator now.
My plan is to put the new ATS between the Main Panel and the sub panel and feed the ATS with the 125 amp breaker
What size would you select for the new generator?
Am I missing something?
I calculated the load on the 125 amp panel at 98 amps using the optional calculation AC larger than heating. The loads are as follows:
General lighting 2774 sq ft @ 3va=8322va First 10000@ 100%= 10000
cook top 5800 Remainder (total-AC load-10kw) = 18888 @ 40%= 7555.20
dryer 5000 AC load @ 100%= 5904
well pump 1656 Total= 23459.20/240 volt=98 amps
disposal 850
dishwasher 1320
Boiler (runs for DHW) 1440
laundry 1500
2 small appliance 3000
AC 5904
Total 34792
I used the square footage @3va for the entire house which gives me a little fudge factor as not all the general use circuits are on the sub panel.
They are using a portable generator now.
My plan is to put the new ATS between the Main Panel and the sub panel and feed the ATS with the 125 amp breaker
What size would you select for the new generator?
Am I missing something?