You can't do this with just KWH. You need billing demand info. Even with demand info. one needs to be careful sizing in this manner depending on the types of load.Can anyone tell me how you would size a generator based off of previous kw hours on a utility bill? Tia
Turn everything they want to run off generator and amp clamp it. Take into consideration of motor loads and can use load shedding.A friend of mine who is an electrical contractor is asking for advice. He has a customer with a 200A service on a 5000 sq ft residence who wants him to install a generator. He has suggested a genny that has a 150A breaker ( I don't know the kW rating), but the customer is balking at the price and wants to save money by getting one with a 125A breaker (likewise). My friend is asking me how he can decide if it will be big enough not to nuisance trip out during peak demand, and there is no demand information available from the utility. This sort of thing is not in my wheelhouse; has anyone have any advice to lend?
This right here. The hell with doing a dumb NEC load calc that's going to make you buy a generator twice as it large as you need.Turn everything they want to run off generator and amp clamp it. Take into consideration of motor loads and can use load shedding.
It would be best to itemize the loads to be served. Sizing the smallest generator that can supply power to those loads is done by assuming that "no load is put ON at the same time".A friend of mine who is an electrical contractor is asking for advice. He has a customer with a 200A service on a 5000 sq ft residence who wants him to install a generator. He has suggested a genny that has a 150A breaker ( I don't know the kW rating), but the customer is balking at the price and wants to save money by getting one with a 125A breaker (likewise). My friend is asking me how he can decide if it will be big enough not to nuisance trip out during peak demand, and there is no demand information available from the utility. This sort of thing is not in my wheelhouse; has anyone have any advice to lend?
didn't get any response to thisHello. What are the risks/ramifications of starting/attempting to start an HVAC system condensing unit pump with an LRA of 109 Amps with a portable genset with a "surge" amps rating of 15KW (6.5A @ 240V)? Instant windings damage? 50 Amp circuit breaker trip? And can "hard start kits" reduce LRA by 50%?
Be patient. If someone wants to respond, they will in their own good time. If nobody has anything to offer, you will get no responses. This is, after all, an all-voluntary forum.didn't get any response to this
Now that I reread your post, it becomes clear that you should not have placed it within an existing thread with its own topic that has nothing to do with your question.didn't get any response to this
ok. Thank you Safepowering.comNow that I reread your post, it becomes clear that you should not have placed it within an existing thread with its own topic that has nothing to do with your question.
I suggest posting a new thread and asking your question there.