Hello, After installing generators and transfer equipment for over 30 years . we have been tasked by our electrical inspectorate to now provide a 30 day analyzer reading to assure the generator is sized appropriately.
The inspectorate is basing this sizing requirement under section 220.87.
Our argument is this code rule is not pertainent to generators. Our installation falls under section 702 of Optional Standby systems. It is also our argument that it is the end users choice as to the size of the generator they want and which loads they choose to operate. It is also our argument that the inspectorate can not enforce a generator to be sized to the full current draw x 125% as per 220.87. We certainly want to to comply with code rulings as they pertain. We just can not see where they are going with this..... Any suggestions on the proper way to size a generator for the full load on an existing building? We typically use an analyzer for a 1 week period and use the average current (not peak) to size our generator installs.
Thanks Guys
The inspectorate is basing this sizing requirement under section 220.87.
Our argument is this code rule is not pertainent to generators. Our installation falls under section 702 of Optional Standby systems. It is also our argument that it is the end users choice as to the size of the generator they want and which loads they choose to operate. It is also our argument that the inspectorate can not enforce a generator to be sized to the full current draw x 125% as per 220.87. We certainly want to to comply with code rulings as they pertain. We just can not see where they are going with this..... Any suggestions on the proper way to size a generator for the full load on an existing building? We typically use an analyzer for a 1 week period and use the average current (not peak) to size our generator installs.
Thanks Guys