I have installed one for a 3hp 240v 1 phase pump motor, I used a 10KW Generac Unit with out any kind of start up or running problems
Please read the below information and it will help you.
Remember, an on-site engine-generator set is a limited source of power, both in horsepower available from the engine, and kVA available from the generator. As such, it must be large enough to start as well as run connected motor loads.
You've lost normal power. Your engine-generator set (gen-set) starts up and reaches speed. Now, you want to start some large motors key to your operation. Suddenly, starter holding coils drop out, starter contacts chatter, and a few motors stall due to insufficient torque for acceleration. Can this happen to you? It sure can, if you haven't sized your gen-set properly.
We all know that motors draw a high inrush current during starting:typically six times full load current. But, inrush currents for the high-efficient motors specified today are almost double that amount. Motors with high inertia loads can also require up to three times rated power during starting.
Yes, it's common for motor starting kVA requirements to determine the size of the set. However, the following factors also play a key role in sizing gen-sets:
?Harmonics caused by variable frequency drives.
?Use of high-efficiency motors.
?Sequential starting of motors.
What's involved. When starting motors, large voltage and frequency dips may occur if the generator set isn't sized properly. Other loads connected to the generator output may be more sensitive to voltage and frequency dips than the motor or motor starter, and this may cause problems. For example, a rate of change greater than 1 Hz/sec in generator frequency may cause some static UPS units to malfunction.
If the load on the generator set is a single large motor, particularly one requiring high starting torque, a number of problems can occur. They include: sustained low-voltage operation that can cause overheating; extended load acceleration times; opening of circuit breakers or motor protective devices; engine-generator protection shutdowns; and more.
Your gen-set's ability to start large motors without excessive voltage and frequency dip is a function of the complete system. This includes:
?The engine power available;
?The generator's capacity;
?The response of the generator excitation system;
?The energy stored in the rotating inertia of the gen-set; and
?The acceleration of the motor and its load.
You must consider all these factors for proper gen-set sizing. Here's a simple rule for estimating the size of an engine-generator set for motor starting: 1kW of generator set rating per each 3/4 to 1 hp of motor nameplate.
Let's look more closely at a motor start. Induction motors have typical starting characteristics. The curve of motor current versus speed shows that during starting, the motor draws approximately six times its full load current; this current remains high until the motor reaches about 80% of speed. This high inrush current causes a dip in generator voltage. The electric power initially required by the motor (with the motor at standstill) is about 150% of rated power. The power required by the motor peaks at about 300% of rated power and 80% of speed with full voltage applied. But, the generator set supplies less than 300% power because starting voltage is lower than full voltage during acceleration, and because the generator set's rotating inertia transfers energy to the motor.
The motor must develop greater torque than required by the load. The motor's torque curve at full voltage is above the load's torque curve. The difference between the torque developed by motor and the torque required by the load determines the rate of acceleration. Since torque is proportional to voltage, any reduction in voltage means a proportional reduction in torque.
A properly sized generator set will support the high starting kVA requirements of the motor, and maintain sufficient output voltage for the motor, so it can develop adequate torque to accelerate the load to rated speed.
All standby gen-sets use synchronous generators with exciters. Many are available with permanent magnet generator (PMG) excitation systems. The PMG provides excitation power independent of the generator terminal voltage. As such, it can maintain full excitation:even during transient loading, such as motor starting. Full excitation power results in a less extensive voltage dip and improved recovery times.
Using reduced-voltage starting. Though a voltage dip often causes various problems, a controlled reduction in voltage at motor terminals can be beneficial, but only when reduction in motor torque is acceptable. Reducing motor starting kVA can reduce the required size of the gen-set, reduce the voltage dip, and provide a softer start for the motor loads. When sizing gen-sets, you must first determine the acceptable level of motor torque required during starting, or the loads will accelerate slowly, or even fail to reach full speed:ultimately causing motor damage.
Using solid-state starters. Solid-state starters can adjust the starting torque, acceleration ramp time, and current limit for controlled acceleration of a motor when it starts. For the purpose of sizing a gen-set, the current limit adjustment reduces the inrush current and may be used to reduce the starting kW and kVA requirement on the generator. The range of available current limit settings is typically from 150% to 600% of full-load current. A 600% current limit setting on the solid-state starter results in a gen-set sizing that's the same as an across-the-line starting. A 300% current limit setting reduces starting kVA by 50%.
Use of the current limit setting also reduces motor torque available to the load. From a gen-set sizing perspective, an extended acceleration ramp time and low current limit setting (if appropriate for the motor and the mechanical load) would result in the least voltage and frequency excursions.
One downside to using solid-state motor starters is their integral SCRs (silicon-controlled rectifiers) will cause voltage distortion. To compensate, you'll have to oversize the generator. The recommendation: two times the running kW load, except where you're using an automatic bypass. If the solid-state starter does have an automatic bypass, the SCRs are only in the circuit during starting. Once the motor is running, the bypass contactor closes and shunts the SCRs. In this case, you can ignore the voltage distortion during starting, and you don't have to add generator capacity.
VFDs require larger generators. All versions of variable frequency drives (VFDs) are current limiting and reduce starting kW and kVA. The current drawn by these drives is nonlinear (having harmonics), which causes a distorted voltage drop across the reactance of the generator. Since VFDs are nonlinear, you must include an additional generator capacity sizing factor to keep voltage distortion to a reasonable level of approximately 15% total harmonic distortion (THD) or less. The larger the generator, the greater the reduction in impedance of the power source (generator), which in turn, reduces the effects caused by harmonic current distortion.
For six-pulse VFDs, a typical generator sizing factor would be twice the running kW of the drive. This offsets any reduction in starting kW and kVA. If it is the pulse width modulated (PWM) type (or includes an input filter to limit current distortion to less than 10%), then you can reduce the sizing factor down to 1.4 times the running kW of the drive.
Using a step starting sequence. The starting sequence of loads can have a significant effect on the size of a gen-set. One commonly used approach is to assume all connected loads will start in a single step. This results in the largest gen-set selection. Unless you do something to add load incrementally (such as multiple transfer switches with staggered time delays, or a step load controller), then you should use a single-step load for sizing purposes.
In multiple step applications, you start the largest motor first, to minimize the gen-set size. Once placing all loads on line with the gen-set, you can stop and start load equipment with automatic controls. Here, you'll have to size the gen-set by assuming the largest motor starts last, with all other connected loads already on line.
Examples of sizing gen-sets. You can size a gen-set with manual calculations (using a worksheet) or with PC software available from most major gen-set manufacturers. The basic process is the same. It's always best to use actual data (if known).
If this information isn't available, using PC software is the best option, since much of the required information on typical load characteristics is available as default information. If you use the manual sizing procedure, it should result in a recovery voltage of at least 90% of rated voltage and a starting instantaneous voltage dip of approximately 20% to 40%.
The instantaneous voltage dip and frequency dip will likely vary from manufacturer to manufacturer, based on equal ratings of gen-sets. For a closer estimation of transient (starting instantaneous voltage) performance, use the manufacturer's sizing software.
Using the manual sizing procedure.
continuing ..........................