How do you properly size a residential standby generator to serve AC and heating loads when using a load shedding service rated transfer switch?
If you are lazy and want to power everything in your home during an outage, crank your AC up to full blast, turn on all the lights, lamps, computers, TVs on in your house. Clamp an ammeter onto the incoming line at the main breaker for your distribution panel in your house. Take that number and multiply by a safety factor and get the next standard size generator above that.
What safety factor do you apply or how is it determined?
Maybe a typo there, 3 kV genset?If I had a house I was installing it in, I would probably just buy a 3kV GenSet (or whatever was on sale) and figure out what I can and can't run while the power is out.
At work I doubled the size of the expected load on a standby GenSet. But then again, I had a few motors running on it and had to go a bit larger to mitigate the voltage drop when dropping load onto the GenSet.
Maybe a typo there, 3 kV genset?
*kW
I can't seem to edit posts... is it not possible on this forum?