I have a generator switchboard (480Y/277) which is fed directly from the 725 KW generator output and set up as an SDS with a bonded neutral and a GEC run to the GES. The plans call for a set of disconnect switches (60 and 400 amp) to be tapped to the line side of the switchboard. A few questions have come up:
1) Are these considered feeder taps or is it treated like a service?
2) How do you size the EGC run with the tap conductors or do you run a neutral conductor and use that to bond all of the metallic parts on the line side of the fused disconnect switches?
3) Is a GEC required to each disconnect.
If this is setup as a non-SDS (bonding jumper removed) I would assume that regular tap rules would apply.
1) Are these considered feeder taps or is it treated like a service?
2) How do you size the EGC run with the tap conductors or do you run a neutral conductor and use that to bond all of the metallic parts on the line side of the fused disconnect switches?
3) Is a GEC required to each disconnect.
If this is setup as a non-SDS (bonding jumper removed) I would assume that regular tap rules would apply.