OK so I have a clinic with a generator on two 4 pole transfer switches. The Engineer didn't do his job right:jawdrop: (gasp)! So I need to address this and want to have my ducks in a row. I am not used to separately derived system transfers.
250(A)(1) requires a bonding jumper between the source and the first "System Disconnecting means". The Generator equipment is an enclosed generator with a 60A and a 400A breaker in the enclosure. Is the first disconnecting means these breakers, or did the engineer mess up even more than failing to put a ground in requiring another means of disconnect prior to the transfer switch, (which I have confirmed is not service rated)?
Quick help would be great.
(tried to attach a picture of the one line, not sure if it did)
250(A)(1) requires a bonding jumper between the source and the first "System Disconnecting means". The Generator equipment is an enclosed generator with a 60A and a 400A breaker in the enclosure. Is the first disconnecting means these breakers, or did the engineer mess up even more than failing to put a ground in requiring another means of disconnect prior to the transfer switch, (which I have confirmed is not service rated)?
Quick help would be great.
(tried to attach a picture of the one line, not sure if it did)