Nec Tap rule 240.21:
26000kw stand-by generator with 125 amp breaker @ generator ,feeds 200 amp # 1 transfer switch in house 20 feet distance,than tap at # 1 transfer switch to # 2 ,200 amp transfer switch (in house)80 feet away, conductors in conduit, would this be against 240.21
445.13(B) reverts back to 240 .21
Install, OCPD at the tap point for conductors longer than 25 feet ,would this satisfy tap rule?
Or is this not feasible.