I am designing a renovation project where I have to make a recommendation on whether an existing generator is in good enough working condition to be kept or if it needs to be replaced. The generator is a CAT 600KW/750KVA, 480Y/277V, Diesel unit with sub-base tank. The gen-set unit is 30 years old but doesn't have a history of any problems and is maintained regularly. I have recommended performing the following testing:
Insulation Resistance Testing on the generator windings.
Infra-red testing on the generator lugs and terminals.
Load bank testing per NFPA 110 requirements.
What other testing or items should be looked at to make a recommendation on this existing generator? How long is the service life of a generator with these characteristics? 40 years?