Hi all,
I'm working a project that came across a unique (at least to me) situation.
Usually when we design a generator to an existing service, there is a service disconnect and if there isn't one, we add one to the line side of the meter. From there we go into the ATS then to the Main distribution panel.
For this project, the service conductors go from the pad mount transformer underground to an MDP (with a main breaker). The client is asking us to remove the connections from the main breaker to MDP's bussing and intercept the line side of the main breaker to feed the ATS from there. Then backfeed the same MDP panel from the ATS through a new breaker on MDP. I've been digging through the code and can only find section 702.12(E) that looks like this might be a violation of. Can anyone tell me if they've seem something similar or if this would be up to code? I'm assuming it's not, but if it is then I'm assuming we would also have to split the neutral bars and ground bars in MDP to keep them separate from the service conductors and the rest of the panel and the main breaker and back feed breaker would have to be interlocked.
I'm attaching a sketch to help visualize what I was trying to describe.
Thanks!
I'm working a project that came across a unique (at least to me) situation.
Usually when we design a generator to an existing service, there is a service disconnect and if there isn't one, we add one to the line side of the meter. From there we go into the ATS then to the Main distribution panel.
For this project, the service conductors go from the pad mount transformer underground to an MDP (with a main breaker). The client is asking us to remove the connections from the main breaker to MDP's bussing and intercept the line side of the main breaker to feed the ATS from there. Then backfeed the same MDP panel from the ATS through a new breaker on MDP. I've been digging through the code and can only find section 702.12(E) that looks like this might be a violation of. Can anyone tell me if they've seem something similar or if this would be up to code? I'm assuming it's not, but if it is then I'm assuming we would also have to split the neutral bars and ground bars in MDP to keep them separate from the service conductors and the rest of the panel and the main breaker and back feed breaker would have to be interlocked.
I'm attaching a sketch to help visualize what I was trying to describe.