I apologize if I seemed somewhat harsh in post #14 but as you've just stated it was an enormous stretch.I'm not going to die on the switch-gear hill, I'll admit it's a stretch.
My whole point was just that a service rated ATS should be readily accessible and fall under the dedicated work-space requirements. This piece of equipment could have three/ four conduits coming out of it which we need clear space for. Furthermore this equipment could potentially be the only means of disconnect for the building or structure. I don't know a good inspector who wouldn't have issue with having one these installed behind a central AC unit or if inside, a wall with less than 3' of front clearance.
I think that maybe were talking about two different things here, one is dedicated equipment space and the other is working space. For an ATS dedicated equipment space does not apply because it is not on the list of 4 items in 110.26(E). Working space applies to items in 110.26(A). A panel above the water spigot would require the dedicated space.