Are there any advantages in having a neutral that is switched vs. a neutral that is not.It seems like a lot of extra work to create a seperately derived system.Is there a good reason for this?
Yes, look at Ed's drawing. The fault has to go back to the N-G bond at the service to return to the generator neutral, which will cuase unbalanced current flow through the service GFP causing a false trip.Originally posted by bennie:
Is the GFP problem the reason for switching the utility neutral?
Yes.When this system is operating on utility power, would a fault on the same feeder also trip the main?