Are there any advantages in having a neutral that is switched vs. a neutral that is not.It seems like a lot of extra work to create a seperately derived system.Is there a good reason for this?
 

brian john

Senior Member
Location
Leesburg, VA
Re: Generator/Transfer switch

Based upon my experience a four pole is best way to go. The reason being; most electrician DO NOT install a three pole ATS and associated generator properly. The neutral is left as shipped from the factory bonded to the generator frame.

And what extra work?
 

bennie

Esteemed Member
Re: Generator/Transfer switch

Ed: Please post the schematic concerning GFI's false tripping when a supply is by a generator.

I would like to print it.

Thank you: Bennie
 

Ed MacLaren

Senior Member
Re: Generator/Transfer switch

Bennie,
I think this is the one you are referring to.

Disclaimer - The following sketch is offered to illustrate basic principles only, and is not intended to represent any actual installation.
Gen12.gif


Ed
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Generator/Transfer switch

Bennie, if you can get your hands on the IEEE Orange Book, look in chapter 7 at the vaious problem configurations of the generators with GFP relays. The problems can be found on both non SDS and SDS.

Good drawing Ed, what's with the disclaimer? :roll:
 

bennie

Esteemed Member
Re: Generator/Transfer switch

Is the GFP problem the reason for switching the utility neutral?
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Generator/Transfer switch

Originally posted by bennie:
Is the GFP problem the reason for switching the utility neutral?
Yes, look at Ed's drawing. The fault has to go back to the N-G bond at the service to return to the generator neutral, which will cuase unbalanced current flow through the service GFP causing a false trip.

If you were to have a site that required two ATS with GFP you can trip the main while on normal supply with no fault what so ever.

[ October 08, 2003, 10:24 PM: Message edited by: dereckbc ]
 

bennie

Esteemed Member
Re: Generator/Transfer switch

When this system is operating on utility power, would a fault on the same feeder also trip the main?
 

Ed MacLaren

Senior Member
Re: Generator/Transfer switch

When this system is operating on utility power, would a fault on the same feeder also trip the main?
Yes.

The following sketch is offered to illustrate basic principles only, and is not intended to represent any actual installation.

Gen15.gif


Ed
 

bennie

Esteemed Member
Re: Generator/Transfer switch

Has anyone calculated the odds of a fault developing while the one feeder is on generator power, when the rest of the load is on utility power?

I think the lottery has better odds.

Usually when the generator is operating, the main system is dead, there would not be any power to dump the breaker.

Neutrals were required to be switched on generator supplied separately derived systems in the 1930's, when they were known as "AC systems without external connections" This was a long time before GFI's were introduced or required.

[ October 09, 2003, 12:01 PM: Message edited by: bennie ]
 