daiashi

Member
Location
NC
Code reference for separating the neutral and ground in a generator
transfer switch.Since its a disconnect and doesn't contain any branch
circuits I don't believe you have to?Its feeding a 100 amp panel witch
I did separate the neutrals. Thanks.
 
daiashi said:
Code reference for separating the neutral and ground in a generator
transfer switch.Since its a disconnect and doesn't contain any branch
circuits I don't believe you have to?Its feeding a 100 amp panel witch
I did separate the neutrals. Thanks.

250.24 Grounding Service-Supplied Alternating-Current Systems
(5) Load-Side Grounding Connections A grounding connection shall not be made to any grounded conductor on the load side of the service disconnecting means except as otherwise permitted in this article.


FPN: See 250.30(A) for separately derived systems, 250.32 for connections at separate buildings or structures, and 250.142 for use of the grounded circuit conductor for grounding equipment.
 