III. Sources of Power
700.12 General Requirements. Current supply shall be
such that, in the event of failure of the normal supply to, or
within, the building or group of buildings concerned, emergency
lighting, emergency power, or both shall be available
within the time required for the application but not to exceed
10 seconds. ..............
Is there a time limit in which a transfer switch has to transfer power from the time regular power is droped? I had an inspector fail me on a final inspection because power transfered in 13 sec. and not 10 sec. The building is a warehouse. Is that in the NEC?