I am currently installing a generator for a customers home. I did this the same way I do all my generators. I put in a sub panel next to the main, installed a 30 amp 2 pole breaker in the main panel and ran a line from the main panel to the generator panel. Then connected that feed to a 30 amp breaker and ran the lines that were to be run off the generator to the generator panel. Then I ran the generator feed into another 30 amp breaker in the generator panel and installed the Square D lock between the two 30 amp breakers that only allows one to be on at a time.
The problem is though on this job the customer has a eb6500 Honda generator. That particular generator is GFCI protected and the kicker is that the neutral is bonded to the frame. So when I turn the power on for the generator the Generator GFCI kicks immediatly Even with no load.
I believe this is happening because the neutral is boded to the generator frame. Obviously the neutrals and the grounds in the home main panel are bonded. My only conclusion on options I can think of would be to find where the netral is bonded to the frame of the generator and dissconect it.
Anyone come across anything like this or have any input to help with this situation? Also why would the neutral be bonded to the frame if this would cause this problem on any residential application? I'm looking forward to the input, thanks.
Mike
The problem is though on this job the customer has a eb6500 Honda generator. That particular generator is GFCI protected and the kicker is that the neutral is bonded to the frame. So when I turn the power on for the generator the Generator GFCI kicks immediatly Even with no load.
I believe this is happening because the neutral is boded to the generator frame. Obviously the neutrals and the grounds in the home main panel are bonded. My only conclusion on options I can think of would be to find where the netral is bonded to the frame of the generator and dissconect it.
Anyone come across anything like this or have any input to help with this situation? Also why would the neutral be bonded to the frame if this would cause this problem on any residential application? I'm looking forward to the input, thanks.
Mike