I have a job I am currently designing. The em service is a separate feed from the utility. THe feed is a 208/120v single phase.
It seems the generator manufacturers make 240/120V single phase or 208/120V three phase Gensets.
Would any of you mix a 240/120V single phase genset with a normal service of 208/120V. They are both connected to the same ATS. The panelboard is an old plug fuse panelboard that is marked as 208V. So I am not sure if it is actually rated for 240V and the 208 was jsut the service voltage marking.
Personally, I do not think it is a good idea to mix the two voltages. It leads to confusion I believe. I also believe the panelboard should be replaced. There is a utility vault that has 480 and 208 3 phase in it. So I cannot get a 240 volt service without major expense. I can get a new 208/120v 3 phase service tho.
The problem is the owner got a quote from an electrician to provide a solution. Then they hired us to do permit drawings. My design is quite a bit more than the electricians. His generator I feel was undersized to begin with, because the chicago code only allows you to have a max of 80% load on an em ltg generator. But that all depends on what load you assume, which is why my other question about VA/SF for em ltg was asked.
Please give me your opinion and if you have a code section about mixing voltages, I would love to hear it.
It seems the generator manufacturers make 240/120V single phase or 208/120V three phase Gensets.
Would any of you mix a 240/120V single phase genset with a normal service of 208/120V. They are both connected to the same ATS. The panelboard is an old plug fuse panelboard that is marked as 208V. So I am not sure if it is actually rated for 240V and the 208 was jsut the service voltage marking.
Personally, I do not think it is a good idea to mix the two voltages. It leads to confusion I believe. I also believe the panelboard should be replaced. There is a utility vault that has 480 and 208 3 phase in it. So I cannot get a 240 volt service without major expense. I can get a new 208/120v 3 phase service tho.
The problem is the owner got a quote from an electrician to provide a solution. Then they hired us to do permit drawings. My design is quite a bit more than the electricians. His generator I feel was undersized to begin with, because the chicago code only allows you to have a max of 80% load on an em ltg generator. But that all depends on what load you assume, which is why my other question about VA/SF for em ltg was asked.
Please give me your opinion and if you have a code section about mixing voltages, I would love to hear it.