I have a 75 kva 480volt 3phase generator no fla is listed so took the kva and converted it to amps with the equation so roughly 90.3 amps. I then multiplied it by 1.15 via nec section 445 so i got 103.75 roughly. Im gonna use 75 degreed column cause thats what lugs rated for. At 1 awg thats good for 130 amps but with 4 to 6 conductors I derated to 104 amps so 1 awg should be good for the 75kva generator anyone see anything wrong with this or is this correct?