I have a 1200 amp 480/277 volt service. The service hits a 1200 amp main breaker enclosure first and the neutral/ground from the padmount is bonded in this enclosure with the underground ground loop. The generator, which my company did not provide, has a 1200 amp breaker installed. The ATS is switching the neutral, which I assume is due to the 1200 amp size. The generator has a logical location for a ground/neutral termination point for lugs to be installed which has continuity to the generator frame/enclosure. This tells me that the neutral/ground is tied to the frame.
The engineer is calling for 4 wires plus a ground from the main breaker enclosure to the ATS and is also calling for 4 wires plus a ground from the generator to the ATS. These runs are 4 parallel runs of #350 with a #2 ground.
The ATS has a ground bar installed that stands alone fastened to the ATS enclosure.
Does this all sound correct? I am not sure where the #2 grounds would terminate at the generator? Should the ground bar in the ATS just be bonded to the exterior ground loop?