warriorelectrician
Member
- Location
- Anacortes Washington
I have a job a customer wants me to do and I pretty sure that is more involved than he thinks. My issue is I have a 400amp CT can outside mounted on a pole not attatched to the building this 400amp service is feeding 3-200amp panels two in the house one to a well house. If I run the feeder wires from the CT can to a 400 amp breaker inside of the automatic transfer switch and I run all the feeders feeding each panel through this transfer switch as well this is now considered the main service equipment (Right?). If this is the case now I have to run ground wires feeding each panel because those are now considered sub-panels. This is what I have done for all of my other installs. This one is a real problem because the pump house is about 500' away and each panel in the house is about 200' away. The only way to add a ground wire would be to pull them out and pull them back in with a ground. Am I right with this or is there another way? Help