We have a four existing diesel drive generators with the following data;
Kw 1200, Kv 6.6, Amps 131.2, Kva 1500, Pf .8, Hz 50, RPM 1000.
These Generators are running/connected to step up transformer of Delta - Y, 6.6 Kv - 11 Kv respectively and this is for the overhead lines.
Now, we have this new Caterpillar Diesel generator set with the following data:
Kw 1200, V 400, Amps 2309, Kva 1600, Pf .8, Hz 50, RPM 1500.
Since the rated output voltage is only 400 volts,
we installed a new step-up transformer Y - Delta, 400 - 6.6 Kv respectively, in order to match with the existing generators with rated voltage output which is 6.6 Kv.
As required, the new generator have all the synchronizing control and protection, the synchronizing control, its sensors such as CT's and the main breaker are intalled between
the Generator and the 400 v - 6.6 Kv( Y - Delta) transformer.The secondary of this transformer is permanently connected with the existing bus of 6.6 Kv.
Take note that this new generator is a Wye output and the Nuetral terminal was connected to the ground and to the nuetral in the primary side of(400V-6.6Kv)transformer
Now the problem is we can not put it online with the other generators, the breaker will only switch on momentarily and tripped, with the errors in our synchrinizing software of Reverse Power.
We able to test this Caterpillar generator alone, online in a dead bus, but the Kvar reading is 200% with 91% effective power.
Is there a possiblity of high circulating current because of this Nuetral to ground connection from the generator?
Can we remove this Nuetral line from generator terminal, anyway we are only stepping up its rated 400v to 6.6 Kv.
Take note: the old generators set have no nuetral out, but only the 3 phase lines going to the 6.6 Kv - 11 Kv transformer.
I appreciated very much of your time and kind help.
Ed
We have a four existing diesel drive generators with the following data;
Kw 1200, Kv 6.6, Amps 131.2, Kva 1500, Pf .8, Hz 50, RPM 1000.
These Generators are running/connected to step up transformer of Delta - Y, 6.6 Kv - 11 Kv respectively and this is for the overhead lines.
Now, we have this new Caterpillar Diesel generator set with the following data:
Kw 1200, V 400, Amps 2309, Kva 1600, Pf .8, Hz 50, RPM 1500.
Since the rated output voltage is only 400 volts,
we installed a new step-up transformer Y - Delta, 400 - 6.6 Kv respectively, in order to match with the existing generators with rated voltage output which is 6.6 Kv.
As required, the new generator have all the synchronizing control and protection, the synchronizing control, its sensors such as CT's and the main breaker are intalled between
the Generator and the 400 v - 6.6 Kv( Y - Delta) transformer.The secondary of this transformer is permanently connected with the existing bus of 6.6 Kv.
Take note that this new generator is a Wye output and the Nuetral terminal was connected to the ground and to the nuetral in the primary side of(400V-6.6Kv)transformer
Now the problem is we can not put it online with the other generators, the breaker will only switch on momentarily and tripped, with the errors in our synchrinizing software of Reverse Power.
We able to test this Caterpillar generator alone, online in a dead bus, but the Kvar reading is 200% with 91% effective power.
Is there a possiblity of high circulating current because of this Nuetral to ground connection from the generator?
Can we remove this Nuetral line from generator terminal, anyway we are only stepping up its rated 400v to 6.6 Kv.
Take note: the old generators set have no nuetral out, but only the 3 phase lines going to the 6.6 Kv - 11 Kv transformer.
I appreciated very much of your time and kind help.
Ed