Existing set up:
400amp 3ph 120/208 feeder to transfer switch Normal Source Terminals from switchgear.
400amp 3ph 120/208 feeder to transfer switch Emergency Source Terminals from Generator, breaker at generator.
400amp 3ph 120/208 feeder to remote panel from transfer switch Load Terminals, wires go into a trough and leave via conduit to panel.
Is it legal to tap the load conductors of the xfer switch that run from the xfer switch Load Terminals to the panel board, go into a breaker and can or fused disconnect, and feed another smaller panel to add some items to the emergency power set up? The total load on the panels does not even come up to half the generator capacity, so load is not an issue. I am discussing this with an engineer and there are different opinions. Please cite code refs to verify legality or not within NEC rules. (2014)
400amp 3ph 120/208 feeder to transfer switch Normal Source Terminals from switchgear.
400amp 3ph 120/208 feeder to transfer switch Emergency Source Terminals from Generator, breaker at generator.
400amp 3ph 120/208 feeder to remote panel from transfer switch Load Terminals, wires go into a trough and leave via conduit to panel.
Is it legal to tap the load conductors of the xfer switch that run from the xfer switch Load Terminals to the panel board, go into a breaker and can or fused disconnect, and feed another smaller panel to add some items to the emergency power set up? The total load on the panels does not even come up to half the generator capacity, so load is not an issue. I am discussing this with an engineer and there are different opinions. Please cite code refs to verify legality or not within NEC rules. (2014)