Hello, I do generator work, and I have a question. If I have a generator and the main breaker inside is a 100 amp, 240 VA, (generator rated at 19.5kW.) Yet my factory sizing guide says it will produce 210 amps, at a 30% voltage drop. (210A X (240X0.70) = 35,280 watts out of a 19,500 watt generator!
To me that approximately 35,280 watts of power, 210 amps is over double the 100 amp main breaker. Am I correct, a inductive or any load exceeding 100 amps or 24,000 watts will automatically trip the 100 amp breaker at 240 VAC, or can it really supply 210 amps? I have people trying to start large AC units with a LRA of 168 amps, I don’t think that’s possible, especially with the 30% voltage drop.
In other words, how fast does a 100 amp main breaker trip with a overloaded? I am sure it depends on the total wattage being used, Can’t seam to find that answer anywhere.
Thanks...
To me that approximately 35,280 watts of power, 210 amps is over double the 100 amp main breaker. Am I correct, a inductive or any load exceeding 100 amps or 24,000 watts will automatically trip the 100 amp breaker at 240 VAC, or can it really supply 210 amps? I have people trying to start large AC units with a LRA of 168 amps, I don’t think that’s possible, especially with the 30% voltage drop.
In other words, how fast does a 100 amp main breaker trip with a overloaded? I am sure it depends on the total wattage being used, Can’t seam to find that answer anywhere.
Thanks...