My generator has a 200amp breaker in it. The service it’s providing is 100amp 480v panel would it be sufficient to run number 3awg from the generator or would I size the wire to the breaker in the generator


Sent from my iPhone using Tapatalk
 
If the installation complies with the appropriate 240.21 tap rule, you can use the #3.
 