Generator

mannyb

Senior Member
Location
Florida
Occupation
Electrician
Recently installed a transfer switch and generator for C Store AC system. The transfer switches isnt a main service disconnect so we used existing disconnect then wiring transfer switch in between. We have a lost a fuse per phase last few days. The generator keeps e everything working and no problems the problem is cause when on utility power. Any ideas why we would loss a phase
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
What type of fuse? Dual element time delay is what you want
Check amps, bolts, IR scan find out what’s changed
Blowing fuse different phase?
 