generator

Status
Not open for further replies.

vf8

Member
i have a home that has 2 paralleled 200 amp feeds under ground into a trough that splits one feed into each 200 amp 30 cir main breaker panel its feed is from transformer and the house has a transformer meter. they have a 25kw generator to be installed (with no room to install any thing)was wondering if i could take one feed into 125 breaker disconnect to the ts switch pull out the 200 breaker in one panel ond main lug it then it would be protected by the 125 generator breaker and the new 125 dis i need to install by moving the ac units over to the other panel the load is only 45 amps

any insight would be greatly appreciated thanks
 
vf8 said:
any insight would be greatly appreciated thanks
#1. Punctuation. Seriously, it's difficult enough to answer questions that are worded well. I suggest reading your posts aloud; when you pause to inhale, insert a comma or period.

#2. Remember that the GEC's for the main-lugged panel must land where its main disconnect (and thus, the bonding jumper) would be relocated: the disco ahead of the TS.
 