Here is why the neutral must be switched when the generator winding center-tap (neutral) is bonded to the frame.I think someone has been fantasizing about why a neutral should be switched in a transfer switch.
It would be a problem in a service, feeder, or branch circuit, and sometimes is, when the grounded (neutral) conductor is bonded to the non-current-carrying metal enclosures at more than one point.When parallel current is no problem on a service, and the entire distribution system, how come it's a problem with a back up generator?
you weren't kidding when you said you were new here.I assume you have some electrical experience
Well this would be stupid without some serious safegarding thru say a UPS.You are responsible for a data center dealing with millions of dollars a minute or an hour, are you wiling to risk the exposure of a possible fault when the site is connected to genset and utility maybe for peak shaving for 8 or more hours, or maybe for one second, time is irrelevant. Murphy won’t risk this and I ain't about too.
First of all how many home owners do you think will properly maintain a back-up generator???Proper maintenance should be performed on all electrical mechanical systems, losing the neutral would be just as bad as an arcing ground fault from a phase conductor, that burns the ATS to scrap. If one can't be confident of the equipment under their supervision they should contract with someone that is. For systems with ground fault protection an ATS with an overlapping neutral properly maintained and TESTED is the way to go IMHO