S sleepy Senior Member Jan 27, 2012 #1 a quick question, startup for a generator, is there a code requirement for the time the generator needs to start up? i have seven seconds? thanks for your help as usual
a quick question, startup for a generator, is there a code requirement for the time the generator needs to start up? i have seven seconds? thanks for your help as usual
pete m. Senior Member Location Ohio Jan 27, 2012 #2 See 700.12 (10 seconds) also 701.12 (up to 60 seconds... with limitations). Depends on which you are asking about. Pete
See 700.12 (10 seconds) also 701.12 (up to 60 seconds... with limitations). Depends on which you are asking about. Pete