fastline
Senior Member
- Location
- midwest usa
- Occupation
- Engineer
Read most of the OSHA and code stuff but still unclear on this. It seems some generators are grounded, some are not. IIRC, a lot of inverters are NOT grounded?
In any case, they indicate a safety concern for bonding a generator. However, if you are running a home with a generator, you WILL be bonding because the N and G are bonded in the main breaker panel.
I have always bonded on generators BUT I am now questioning if you don't disconnect the N from the POCO with a transfer switch and only disconnect the main breaker, is there a concern there?
All in all, I m just trying to determine how most generators are connected, how to verify quickly ( I assume just resistance test on the leads, not running?), and how things should be connected.
In any case, they indicate a safety concern for bonding a generator. However, if you are running a home with a generator, you WILL be bonding because the N and G are bonded in the main breaker panel.
I have always bonded on generators BUT I am now questioning if you don't disconnect the N from the POCO with a transfer switch and only disconnect the main breaker, is there a concern there?
All in all, I m just trying to determine how most generators are connected, how to verify quickly ( I assume just resistance test on the leads, not running?), and how things should be connected.