Talked to a sales rep supplying generators and UPS gear.
He said they always require ground rods at all generators.
1) If the grounded conductor is not switched at the ATS, and there's a EGC run with the phase conductors - doesn't a ground rod give a second path to ground?
This seems like a second system bonding jumper with respect to the OCPD trying to clear a fault.
250.35 (B) Permanent and nonseperately derived generators.
He said they always require ground rods at all generators.
1) If the grounded conductor is not switched at the ATS, and there's a EGC run with the phase conductors - doesn't a ground rod give a second path to ground?
This seems like a second system bonding jumper with respect to the OCPD trying to clear a fault.
250.35 (B) Permanent and nonseperately derived generators.