mallard duck
Member
- Location
- Maryland
We have two (2) 300 kVA, 120/208 V Genset each paralleled into Asco 7000 series transfer switch. Transfer switch is rated 1200 A. The load side of transfer switch is connected to 1200A panel board bus. Normal power from utility is from secondary side of 300 kVA, 120/208 V transformer. In the event of normal power failure both the generators paralleled could dump 1666 A into 1200 A rated transfer switch.
The contractor sayes that because the load will be less than what the generators can put out and the load should never exceed 1200 amps it meets code.
My problem is there is a small possiblity it could and the generators would then exceed the listed lable on the transfer switch and the main distribution panel. Does this meet NEC?
The contractor sayes that because the load will be less than what the generators can put out and the load should never exceed 1200 amps it meets code.
My problem is there is a small possiblity it could and the generators would then exceed the listed lable on the transfer switch and the main distribution panel. Does this meet NEC?