Senior Member
- Location
- SW Florida
It has been determinded by my AHJ that generators installed with ATS shall be sized to supply 100% of the connected load. MTS systems need not be sized to total load but individual circuit breakers in the panal must be marked as Generator circuits. This decision was made after addending a Emergancy Generator Seminar shich I did not attend. Demand calcs are required for the sizing of the Generator, ATS, Feeders that feed the panel being used. I think this is a wonderful idea as when the 15KW gen starts up and feeds a loaded 200 amp panel, the 70 amp breaker will trip and therefor no power. Most of these homes are not occupied durning the summer months when it is likley to be needed therefor no body to reset and turn off unnessary circuits. A/C, Refridgeration, pool pumps, security systems, etc will be out. Any thoughts or code referances to justify this requirement?