Generic power factor

Status
Not open for further replies.

arnettda

Senior Member
Can you have a power factor of above 1 ? If ot above one, If kw equals volts x Amops x 1.73 x power factor what is wrong with using a power factor of 1?.I never remember hearing of having a power factor above 1 .
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Can you have a power factor of above 1 ? If ot above one, If kw equals volts x Amops x 1.73 x power factor what is wrong with using a power factor of 1?.I never remember hearing of having a power factor above 1 .
Given the formal definition of power factor as the instantaneous power integrated over time divided by the product of the RMS voltage and the RMS current, you can prove mathematically (just a little algebra and a little calculus) that PF cannot be greater than 1.
And that you get 1 only when the current waveform is an exact match to the (not necessarily sinusoidal) voltage waveform.
That corresponds to a linear resistive load.

Sent from my XT1585 using Tapatalk
 

Besoeker

Senior Member
Location
UK
Can you have a power factor of above 1 ? If ot above one, If kw equals volts x Amops x 1.73 x power factor what is wrong with using a power factor of 1?.I never remember hearing of having a power factor above 1 .
You can use a PF of 1.0 if the load is purely resistive with no reactive components and zero harmonics. Not altogether common, at least in my experience, to get that.

And, as GD has said, you can't have a PF greater than 1.0.
 

kwired

Electron manager
Location
NE Nebraska
You can have a power factor that is leading instead of lagging though.

A circuit with a capacitor only would have a leading power factor.
 

kwired

Electron manager
Location
NE Nebraska
Yes, but close to zero.
That depends on the KVAR of the capacitor just like power factor of a motor depends on KVAR of the motor.

If you have a motor with KVAR of 10 and apply 20KVAR correction capacitor - you still end up with a net of 10 KVAR in your circuti - but it went from lagging power factor to leading power factor.
 

Besoeker

Senior Member
Location
UK
That depends on the KVAR of the capacitor just like power factor of a motor depends on KVAR of the motor.

If you have a motor with KVAR of 10 and apply 20KVAR correction capacitor - you still end up with a net of 10 KVAR in your circuti - but it went from lagging power factor to leading power factor.
I was responding to your
A circuit with a capacitor only
comment.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Mathematically it would be impossible. Power is a vector which has magnitude and direction. The power factor is derived by taking the cosine of the angle (direction). The cosine of 0deg is = 1.0 In this case the KW = KVA, The cosine of 90 deg = 0; thus KW is zero and KVAR = KVA. At 91 deg, the value will take on a negative value which means it is now leading instead of lagging; and all the way until 180 deg, but never more than -1.

Basically, it's a whole bunch of trigonometry thus the range will always be between 0 to 1.0 which is termed lagging, and between 0 to -1 which is termed leading.
 

Ingenieur

Senior Member
Location
Earth
pf = active power P / total power S
active power = perform work
total power S = active power + reactive power = P + jQ
|S| = sqrt(P^2 + Q^2), even if Q = 0 then S = P and pf = P/P = 1

if pf > 1 that means you are getting out more active power/work than the total you put in
not happening
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Can you have a power factor of above 1 ? If ot above one, If kw equals volts x Amops x 1.73 x power factor what is wrong with using a power factor of 1?.I never remember hearing of having a power factor above 1 .
As others have said, PF cannot be >1.00. PF is a measure of how well AC voltage and current are aligned in the time domain. If they are perfectly aligned, PF = 1.00. If the current waveform shifts either way relative to the voltage waveform, PF < 1.00.
 