Hi everyone,
I came across a 800Amp 120/240V Delta Switchboard that has a service rated 600Amp ATS being used as the Main disconnect, unfused, I have never ran into this before. There is a disconnect for the distribution section after the transfer switch.
In a emergency situuation, you would have to open the ATS, clip the cable tie holding the handle, screw it into the manual bypass, switch the control to manual and shut it off, keeping in mind this part of the panel would be only protected by the 100amp fuse located on the pole fed by the 12kv... Seems like a lifesafty issue to me, but maybe I am just overreacting? The Swithcboard was installed in 2020.
as a side story:
Which makes this a more complicated problem, the customer is wanting to add a battery backup to their solar, so it would intail tapping into the ATS with another ATS to bypass the 250KVA Genset, running 350mcm 200' to the PV and battery pack and back to the ATS. Of course this would be on the utility side, so a fused disconnet would have to be installed... Also the changeover will be a logistical nightmare, having to get the modifications of the Switchboard approaved, while keeping the lights on...
Thanks,
Jon
I came across a 800Amp 120/240V Delta Switchboard that has a service rated 600Amp ATS being used as the Main disconnect, unfused, I have never ran into this before. There is a disconnect for the distribution section after the transfer switch.
In a emergency situuation, you would have to open the ATS, clip the cable tie holding the handle, screw it into the manual bypass, switch the control to manual and shut it off, keeping in mind this part of the panel would be only protected by the 100amp fuse located on the pole fed by the 12kv... Seems like a lifesafty issue to me, but maybe I am just overreacting? The Swithcboard was installed in 2020.
as a side story:
Which makes this a more complicated problem, the customer is wanting to add a battery backup to their solar, so it would intail tapping into the ATS with another ATS to bypass the 250KVA Genset, running 350mcm 200' to the PV and battery pack and back to the ATS. Of course this would be on the utility side, so a fused disconnet would have to be installed... Also the changeover will be a logistical nightmare, having to get the modifications of the Switchboard approaved, while keeping the lights on...
Thanks,
Jon