Genset Breaker to Switchgear Grounding

dcreaney

Member
Location
Darien, Wi
Occupation
Electrical Engineer
Greetings,

I have a genset enclosure that has a 2500KW generator with a 4000A breaker that feeds a 4000A switchgear inside the enclosure. I am running (10) 444KCMIL DLO cables per phase and neutral and (2) 444KCMIL DLO cables per ground. The cable is routed from the genset to the switchgear in 2 layers of cable tray, (2) 444KCMIL DLO per tray. I have always sized the ground per NEC 250.66 grounding electrode conductor. I have an inspector that is saying these grounds need to be sized per NEC 250.122 (F) (1) equipment grounding conductors. So, I am curious which code would apply to this application.
 
Pet peeve here-
Are you using actual DLO (not an NEC cable type) or are you using a fine-stranded dual-listed cable that's also RHH/RHW-2? (Or why not just use THHN can be done with it? Or another NEC fine-strand type like W? If you don't need the 2kv insulation you're wasting money on it.)
 
Pet peeve here-
Are you using actual DLO (not an NEC cable type) or are you using a fine-stranded dual-listed cable that's also RHH/RHW-2? (Or why not just use THHN can be done with it? Or another NEC fine-strand type like W? If you don't need the 2kv insulation you're wasting money on it.)
Using a UL listed RHH/RHW that is also TC rated.
 
OK, so you're not using DLO, you're using RHH/RHW. I'm still curios why you're using that and not some other cable.

One end at the generator and one at the switchboard.
Where are those terminating- on a ground bus at each end or ???? (Where is the N/G bond of the system? Is there on at the generator or is it in the switchboard? Another way to look at this- is the generator a Separately Derived System or not?)
 
OK, so you're not using DLO, you're using RHH/RHW. I'm still curios why you're using that and not some other cable.


Where are those terminating- on a ground bus at each end or ???? (Where is the N/G bond of the system? Is there on at the generator or is it in the switchboard? Another way to look at this- is the generator a Separately Derived System or not?)
That is the type of cable that the customer has specified for the job.

They both terminate at bus bar and the N/G bond is at the genset.
 