Greetings,
I have a genset enclosure that has a 2500KW generator with a 4000A breaker that feeds a 4000A switchgear inside the enclosure. I am running (10) 444KCMIL DLO cables per phase and neutral and (2) 444KCMIL DLO cables per ground. The cable is routed from the genset to the switchgear in 2 layers of cable tray, (2) 444KCMIL DLO per tray. I have always sized the ground per NEC 250.66 grounding electrode conductor. I have an inspector that is saying these grounds need to be sized per NEC 250.122 (F) (1) equipment grounding conductors. So, I am curious which code would apply to this application.
I have a genset enclosure that has a 2500KW generator with a 4000A breaker that feeds a 4000A switchgear inside the enclosure. I am running (10) 444KCMIL DLO cables per phase and neutral and (2) 444KCMIL DLO cables per ground. The cable is routed from the genset to the switchgear in 2 layers of cable tray, (2) 444KCMIL DLO per tray. I have always sized the ground per NEC 250.66 grounding electrode conductor. I have an inspector that is saying these grounds need to be sized per NEC 250.122 (F) (1) equipment grounding conductors. So, I am curious which code would apply to this application.