Genset epss intitial load bank test

Status
Not open for further replies.

ktgriffin8

Member
Location
Dallas, Texas
AHJ (Fire Marshal) ran the intial start up "backwards" and passed the generater. According to 2010 NFPA 110 7.13.4.1.3 (10) intended load and 7.13.4.3 equal to 100 percent. AHJ ran the 1.5 hours at 100%. After cool down he ran a 2 hour with the intended load. Is this an issue? Or does 7.13.4.1.3(2) no minimum load help.The generater is for a nursing home and subject to HHSC state inspection.
 