We are installing a 60KW genset. 3 phase 4 wire 208 volt with underground conduit from genset to inside a commercial building and into an ATS. I calculated the output to be 167 amps. there will be a circuit breaker on the genset outside (factory installed on unit). The neutral will not be switched in the ATS so this will not be a separately derived system.
My question is, does the copper power conductors from the generator to the ATS need to be sized 125% of the rated output of generator (4/0 copper THWN) or will 3/0 THWN be compliant. The generator will power general lighting, receptacles, heating systems and IT department.
Thank you.