hhsting
- Glen bunie, md, us
- Junior plan reviewer
I have genset that feeds service rated Fire Pump ATS/controller all in one. The drawing does not indicate the poles of the ATS. Their is no neutral run between the fire pump ATS/controller only equipment grounding conductor and phase conductors are run from genset to the fire pump controller/ATS.
The service rated Fire pump ATS/controller on normal side is fed from utility and has neutral to ground bond.
My questions are as follows:
1. If its 4 pole Fire pump ATS would the genset need to be grounded with grounding electrode conductor? I mean genset would be considered separately derived but no neutral is provided so how can their be neutral to ground bond and grounding electrode conductor from neutral at genset? Does equipment grounding conductor need to have grounding electrode conductor in that case?
2. If its 3 pole Fire Pump ATS then genset would be consider non separately derived I would run only equipment grounding conductor?