This is a problem why?.... I have seen where guys cut them off inside the connector....
Field Inspection Guidelines for MCAP cable
Here is a list of details to verify for when inspecting
installations of MCAP and HC MCAP cables.
? Aluminum ground conductor cut flush with armor
? MC Cable Fitting packaging marked MCI-A
From Southwire
spiralling it is tricky. To get the mc split, antishort bushing installed, tracerwire spiral (going with the ridges on the sheath, and then put into a connector is a bit more time consuming than normal mc. the tracer wire, if properly wound around the cable to allow the connector to fit properly on it, would be visible above the connector. I have seen where guys cut them off inside the connector and it makes for a very poor mechanical connection between the connector andmc.