Re: Geothermal...
1793, As John C says, the Geo thermal is basically driven from an energy exchanger system such as a heat pump split system. The supplemental heat elements are interum heating until the refrigerant exchange gets up to speed.
Your concern as i understand is the elements needed and the feeder to match. The heating call is the HVAC contractor's sizing for compliance to the local AHJ climate zoning specifications and house conditioned volume.
There is a possible Murphy 'gotcha' if the specs show the unit as a 2 or 3 stage and the HVAC only installs minimum code. The feeders should be sized for the capability to meet the unit overall specs.
Compressor tonnage (1 ton= 12 kBtu or 3.5 kW) is the key to matching what is needed for the living area volume in the Climate Zone requirement per the local AHJ permit. (i.e. For a 2000 sf house in North West sea level locations a 700 sf per ton or 3 ton heat pump is generally adequate.) Size the start up stage elements on the high side for higher elevation Zone 2 areas for quick heat response using something like a 15 kW (5kw + 10kw) combination. For considering lesser climate zone requirements and higher compressor exchange rate efficiency an 10 seer is generally energy code minimum compared to a higher 16-18 seer rating. A scrolled compressor only uses one motor for both fan and refrigerant exchange functions.) The interior air handler is separate and has an additional feed. A 60a, 240v 1 ph for 10kw, 30a for 5kw, 40a disconnect will handle 3 ton compressor loads easily. Again, this is based on a smaller house as compared to other size standards and in different areas.
rbj ,Seattle