1st photo from an old home with alot of homemade wiring - not an infrared camera, just kept the flash and lights off. Who ever installed had the #14 wire connected upstream of the main breaker for the apartment (3 family home). Had to turn off all power to the building - within a minute after doing that the wire disintegrated and broke. Alot of heat damage to the terminal bar that it was connected to.
2nd and 3rd photos - new construction with a terminal bar that is crooked in vertical direction - this is the section that is closer to the front of the panel. Can this indicate that something is loose or was the terminal bar smacked around alittle after install?
http://i15.photobucket.com/albums/a352/TonyPE/IMGP4801_edited-1.jpg
http://i15.photobucket.com/albums/a352/TonyPE/IMGP4843_edited-1.jpg
http://i15.photobucket.com/albums/a352/TonyPE/IMGP4844_edited-1.jpg