StevenLeuck
Member
- Location
- Eugene, OR, USA
We have a large multi-family mixed use building we are just now bringing out of the ground. We're trying to figure out a solution to the over-sized conductors on too-small lugs. All of our residential units require only a 100Amp loadcenter. We've solved the connection at that end of the feeder by buying 150A rated MLO loadcenters which have lugs good for up to 300KcMIL. However, it's the other end that has me concerned. The meter/main meter packs we're using are Eaton (Cutler-Hammer) and the 2-pole mains will be BR2100 circuit breakers. Submittal sheets say the maximum wire size on their lugs is 1/0. However, due to distances, we have about half the building requiring #2/0 feeders, plus a small handful of them at both #4/0 and #250KcMIL. I've been researching ways to reduce the conductor size to fit on the 1/0 lugs but not finding anything conclusive. Am curious to know what others have done as inevitably, there are others who have run into this before us. I can't find any manufacturers who make a compression reducer that will go from 250 to 1/0. Mechanical lugs are plentiful for this. I'm hoping I can find out from others what they've done in the past. Also curious about code quotation to back us up with the inspector for having 10' of 1/0 AL at the beginning of a #250 AL feeder in case they have a problem with it.