For some reason, when I try to ask for the source impedance from the utility company(Entergy), they keep telling me they cannot give the info because of liability reasons.
However, i need to know that info in order to get the lower bounds of my arc flash calculations.
the sometimes provide - maximum phase to phase short circuit fault, however a minimum is needed for proper protection.
** a min value could be used to calculated Zsource.
Ibf-min = Isc-min = FLA/(Zsource+Zxfmr)*100
Log(Ia-min) = 0.662*Log(Ibf-min)+0.966*V+0.000526*G+0.5588*V*Log(Ibf-min)+(-0.00304*G*Log(Ibf-min)+K)
How do you guys typically deal with this issue?