I have a hospital that was designed with two levels of GF protection per 517-17a (1999 NEC) the incoming service is 4W with GF Protection but (2) of the (5) branch breakers are only fed with 3W and feed a 3 pole transfer switch (The breakers are set up with GF Protection). Since there is not a neutral conductor the GF will not work.
My question is this: How far do we need to carry the neutral conductor to make this system operate correctly. Do we need to change the transfer switch out to a 4 Pole since there is currently (1) 600A 4 pole transfer switch in the distribution system.
Here is how it is currently set up: Main switchboard 125A GF Circuit breaker feeds a 3 Pole 125A transfer switch (3 Phase 3 Wire). The transfer switch then feeds a 75KVA dry type transformer (3 Phase 3 Wire). Which then feeds a 225A 3P 4W Panelboard. {Also the feeder from the generator switchboard to the 125A 3 pole transfer switch is 3 phase 3 wire}
Thanks,
Ed
My question is this: How far do we need to carry the neutral conductor to make this system operate correctly. Do we need to change the transfer switch out to a 4 Pole since there is currently (1) 600A 4 pole transfer switch in the distribution system.
Here is how it is currently set up: Main switchboard 125A GF Circuit breaker feeds a 3 Pole 125A transfer switch (3 Phase 3 Wire). The transfer switch then feeds a 75KVA dry type transformer (3 Phase 3 Wire). Which then feeds a 225A 3P 4W Panelboard. {Also the feeder from the generator switchboard to the 125A 3 pole transfer switch is 3 phase 3 wire}
Thanks,
Ed