zog Senior Member Location Charlotte, NC May 12, 2006 #1 Anyone know what year the requirent for GF protection for 150-600V 1000A and above disconnects was put in the NEC? Would a facillity built before this be "grandfathered"?
Anyone know what year the requirent for GF protection for 150-600V 1000A and above disconnects was put in the NEC? Would a facillity built before this be "grandfathered"?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) May 12, 2006 #3 My oldest code book dates back the 1987 NEC and 230-95 is present in that book.
zog Senior Member Location Charlotte, NC May 12, 2006 #4 Thanks infinity, I think the facillity was built in 1988, so that should do it.
steve66 Senior Member Location Illinois Occupation Engineer May 12, 2006 #5 Per the handbook, GF protection on services was first required in the 1971 code. Steve