Q: If the GFCI can detect the low fault level current then why the AFCI is needed for such a condition sometimes in branch circuit?
GK
GK
haskindm said:GFCI detects an imbalance in a circuit - more power going out on the hot than is returning on the neutral conductor, for example. Standard breakers and GFCI's see an arcing fault as a load. Unless this fault creates a large enough current draw to trip the device it will remain energized. AFCI's look for the abnormal sine wave that is created by an arcing fault and open when it is detected. They also have a higher level ground fault detector that will open the circuit if there is an arc to ground or neutral. The two devices do separate jobs using very different methods.